The fuse is there to protect BOTH the device and the wiring.  It
should NEVER exceed the rating set by the device manufacturer which
will usually have a bit in reserve.

> Picking fuse/breaker ratings with respect to the device's nominal
> current draw may not allow for inrush current.

Use an anti-surge or Slo-Blo fuse.


> OTOH, if wire size selection has been conservative, I'd use caution
> in placing too high a fuse/breaker rating on something that's really
> expensive.  Sometimes an avionics mfr. will specify even 16 ga. be
> used on the 14V line, even though the box draws, say, 1.3 A.  But if
> the fault inside were to kick the draw to just below a 10-amp
> fuse/breaker, you could be slowly cooking component$ inside that are
> not initially defective and frying traces off a PCB board.

I agree absolutely, but not just the expensive equipment.  I've seen
clouds of fumes coming out of a ham transmitter than had been fitted
with a 10 amp fuse after the original 5 amp fuse had blown.  I don't
know how toxic the fumes were but they certainly reduced visibility.

Please, take great care.

Peter Barwick


********************************************************************
 This message and any attachments are confidential to the ordinary
 user of the e-mail address to which it was addressed and may also
 be privileged. If you are not the addressee you may not copy,
 forward, disclose or use any part of the message or its
 attachments and if you have received this message in error, please
 notify the sender immediately by return e-mail and delete it from
 your system.

 Internet communications cannot be guaranteed to be secure or
 error-free as information could be intercepted, corrupted, lost,
 arrive late or contain viruses. The sender therefore does not
 accept liability for any errors or omissions in the context of
 this message which arise as a result of Internet transmission.

 Any opinions contained in this message are those of the author and 
 are not given or endorsed by the HSBC Group company or office 
 through which this message is sent unless otherwise clearly 
 indicated in this message and the authority of the author to so 
 bind the HSBC entity referred to is duly verified.

********************************************************************


<Prev in Thread] Current Thread [Next in Thread>